No, the calibration means you connect two diferent voltages to the same channel (not in the same time) and inform the card wich voltage you connected. 24b8vin 0 cal 1 5 for 5V connected to channel ...
No, the calibration means you connect two diferent voltages to the same channel (not in the same time) and inform the card wich voltage you connected. 24b8vin 0 cal 1 5 for 5V connected to channel ...
Hi, The latest firmware version is 1.4. Calibration must be done at two points to be complete. The two points must be as close as possible to the two ends of the measurement scale for good results.